diagram for soft stater ?
Answers were Sorted based on User's Feedback
Answer / rites
diagram is simple if u can imagine
3 phases are connected to incoming side
output 3 phases are connected to motor (motor in delta)
in each phase there are antiparallel connected thyristors.
all these thyristors firing angle is slowly changed to make
full voltage available to the output.
so what softstarter is doing applying gradually increasing
voltage up to rated to motor.
there is no control over frequency or current.
Typically take 5 to 20 seconds to ramp up.
Is This Answer Correct ? | 8 Yes | 1 No |
well... here we cant post such a diagram. soft starter
nothing but a starter. if will be connnected parellen with
normal DOL stater. and soft stater contacter and DLo
starter would be interlocked electricaly and mechanically.
At starting when u press the starting button the soft
starter contactoe will be closed when motor reach normal
running automativally (time setting) the S/S contactoe will
drop down and DOL starter contactor wil pick up. then motor
wil keep on running in DOL starter.
Is This Answer Correct ? | 5 Yes | 3 No |
No one can give u such diagram, unless there is some commercial implications. For your kind understanding,
softstarter is nothing but a variable transformer, can be
of conventional type, or modern triac based. The
requirement is to vary the supply voltage applying to a
high capacity motor.
Is This Answer Correct ? | 6 Yes | 6 No |
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
What is the tension required for the 25000 CFM AHU belt
what is the working principle of contactor and conditions of normal open and normal close on it?
can we measure +,-.zero sequence current ....? if so how can ???
1. Can a 12v DC choke operate a 60v/12w PL lamp ? 2. Can a 230v ballast fire / operate a 60v/12w PL lamps.
0 Answers ICS Integrated Computer Solutions,
sir, i want to know the calculation for find rated current for cable sizes.(both copper & aluminium) with examole. please sir for example: 35sq.mm al.cable is withstands for how many amps? is suitable for 45kw motor?
why transformer calling in VA rating
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
out of all machines which have highest efficiency and why?
Percentage losses in power generation?
what must be the mf for a meter with the following conditions. line ct ratio-100/1 line pt ratio- 220kv/110v meter pt ratio- 3X63.5V meter CT ratio- -/1 A
1 HP = how many Kva