What are Line losses and how can be it minimized/controlled.?

Answers were Sorted based on User's Feedback



What are Line losses and how can be it minimized/controlled.?..

Answer / rk

T&D Losses= (Energy Input to feeder(Kwh)-Billed Energy to Consumer(Kwh)) / Energy Input kwh x100
Distribution Sector considered as the weakest link in the entire power sector. Transmission Losses is approximate 17% while Distribution Losses is approximate 50%.
There are two types of Transmission and Distribution Losses
Technical Losses
Non Technical Losses (Commercial Losses)

Is This Answer Correct ?    1 Yes 0 No

What are Line losses and how can be it minimized/controlled.?..

Answer / abc

There typically two types of losses in line T&D.

1. Technical Losses

The technical losses are due to energy dissipated in the conductors, equipment used for transmission line, transformer, subtransmission line and distribution line and magnetic losses in transformers.

Technical losses are normally 22.5%, and directly depend on the network characteristics and the mode of operation.

The major amount of losses in a power system is in primary and secondary distribution lines. While transmission and sub-transmission lines account for only about 30% of the total losses. Therefore the primary and secondary distribution systems must be properly planned to ensure within limits.

The unexpected load increase was reflected in the increase of technical losses above the normal level
Losses are inherent to the distribution of electricity and cannot be eliminated.
There are two Type of Technical Losses.


1. Permanent / Fixed Technical losses

Fixed losses do not vary according to current. These losses take the form of heat and noise and occur as long as a transformer is energized
Between 1/4 and 1/3 of technical losses on distribution networks are fixed losses. Fixed losses on a network can be influenced in the ways set out below
Corona Losses
Leakage Current Losses
Dielectric Losses
Open-circuit Losses
Losses caused by continuous load of measuring elements
Losses caused by continuous load of control elements

2. Variable Technical losses

Variable losses vary with the amount of electricity distributed and are, more precisely, proportional to the square of the current. Consequently, a 1% increase in current leads to an increase in losses of more than 1%.

Between 2/3 and 3/4 of technical (or physical) losses on distribution networks are variable Losses.
By increasing the cross sectional area of lines and cables for a given load, losses will fall. This leads to a direct trade-off between cost of losses and cost of capital expenditure. It has been suggested that optimal average utilization rate on a distribution network that considers the cost of losses in its design could be as low as 30 per cent.
Joule losses in lines in each voltage level
Impedance losses
Losses caused by contact resistance.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

In a 3 phase 4-wire system. For a 3.5 core cable if all loads are single phase and balanced, what will be neutral current? will it be sum of all phase currents? Or it will be zero? And if loads are unbalanced what will be neutral current?

0 Answers  


Why OLTC(On Load Tap Changing)transformer is not recomended for improving voltage instability?

2 Answers  


Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.

1 Answers  


can we use 220 volt 15 w a.c. lamp on 220 volt d.c.

6 Answers   TCL,


How to check the LM324 Ic

0 Answers  






What is ment by KVAR and what are the advantage&dis- advantages of KVAR

2 Answers  


what does happen if generator frequency fall in running condition & what should require immediately

4 Answers  


what purpose of the percentage impendance in transformer

3 Answers  


What is frantic effect?

0 Answers  


In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected

3 Answers  


HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED

6 Answers  


For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.

23 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)