How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 29 Deg C)?
Answers were Sorted based on User's Feedback
Answer / ashwin patel
111 ohm as,
Rt=R0(1+αt), where α=0. 00385, R0=at 0°=100ohm resistance for PT100,
Rt=100(1+(0.00385*29))
Rt=100(1+0.11)
Rt=100*1.11
Rt=111ohm
| Is This Answer Correct ? | 3 Yes | 0 No |
please suggest me, how can i change the display setting in term of unit in place of % of Honeywell pressure transmitter ST3000S100?
How Control valve sizing is done?
What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?
Exapain Deatails of the PID controlller
what type of cables are used for f&G systems and detectors, what is the standard colour?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
what is the calibration standard for pressure and differential pressure transmitters?
How to calibrate the pressure Transmitters
How to set up the various advanced process controllers, input the proper parameters, and tune those controllers given related control system information.
What is the difference between HMI and SCADA and MMI
can we connect instrument earth pit to electrical earth pit, if not why?
An RTD is a_________________________.it works as follows
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)