Answer / prashant soni
HT Cable size dependson fault level to be withstood and its duration..
If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.
This will give you min. size required for HT system (11/22/33/6.6/3.3kV)
Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ahmed
how many cable shoul be connected for 2000kva transformer of 11kv.
primary 3*240 sqmm AL cable
Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase
(N1,N2,N3 & N4) Neutral
Is This Answer Correct ? | 2 Yes | 2 No |
when a primary current injection test is required, it is accomplished by what?
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
what is the function of conservater in transformer
why occ characteristics of generator is also called as magnatization characteristics
hi , i have 150 kw loud and we need 50 m cabil,i want to know wich size cabil we use. thanks
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
how flow current in 220 kv line to line
what are difference between indoor and out door substation
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
why the transformer primary terminal indicated by u,v,w.to technical reason
why we are grounding the neutral?
How to test lightning Arrester?