my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
Yes there's a thumb rule for cable size calculation for 1sqmm Aluminum cable can carry 2Amps and 1 Sqmm Copper wire can carry 4 Amps.
However the cable size increase above 100 Sqmm this thumb rule can not be considered. You need to refer the cable size calculation chart.
Is This Answer Correct ? | 0 Yes | 0 No |
HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM
how much watts are equal to one unit of energy meter?
Can neutral line also be use as a earthting for distribution transformer, or we need separate earthing pit forh the transformer?
In CT, burden is 15 VA and protection 5P20,CT ratio is 100:1 then what would be the knee point voltage ?
Lt trivector meter with ring type CT.Spec of meter are 3x240 v, -/5A. Ring ct spec. are 60/5A, line voltage- IL .66/3.0KV..what is the multiplying factor
Why the capacitor bank is keeping on for electricity supply and keeping it off for generator supply
Whot is the difference between MCB and MCCB.Whot is the selection critearea for MCCB and MCB for 63 Amp.
ups and invertor battery selection chart and full formula
what is resver in electrical enginnering with answer
what happened if power factor is "1"
pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?