Answer / kumaran
1.The magnetic flow meter should not shows the error if it is properly grounded and properly terminated with transmitter.
2.Always the installation should be made like valves before and after the sensors. while showing error in the meter, you should close the downstream and upstream valves to check the zero. If it is shows zero then there is no error in the zero point.
3.Check the span error by weihging the flow. the sensor output pipeline should be connected to the tank and measure the tank area, fill the tank and check the span between tank capacity and the flow rate.
4.make sure that the observing coils inside the sensors are clean. else try to clean the same.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / cbell
short circuit the two electrode (E1 and E2) in the terminal and adjust the zero (4 ma)
Is This Answer Correct ? | 0 Yes | 0 No |
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
how to make a calibration for differential pressure
how to control pid
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
what is the difference between E/P positioner and I/P positioner in control valve , in which application the respective positioner are used in.
define optical temperature detector
What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?
3 Answers Bajaj, Kohinoor, Wartsila,
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?
Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please
can you give some devices that measure directly the mass flow rate.
Q-Explain the different load conditions that will produced different offset which may or may not be acceptable to thhe control function