Sir, my yokugava FF TYPE LEVEL transmitter us bad, i don't have spares available, i want to replace it with a Rosemount FF transmitter, please tell me what procedure to be followed and what changes to be done in dcs part.
Answer / rajesh.
If the device calibration range is alike, and all required instrument data are match, we can use. We need to change instrument details like model#, serial#, make etc. in DCS engineering station. Upload, and down load data to communicate it online. And proceed to check as LEVEL both side in field as well as in DCS panel.
Is This Answer Correct ? | 2 Yes | 0 No |