if suppose boiler has high heavy tube leakage, so in which time we feed the water in a boiler. can we stop the feed water at particular combustion temperature.
Answers were Sorted based on User's Feedback
Answer / mayur mukaty
In normal operation if boiler feed pump stop within a 1 min level goes down to become zero. For best practices when tube leakage heavily fuel feeding stop, take down the load, maintain draft , and take manually FRS system to maintain drum level as for as possible. For latest technology improvement ultra sonic senser are deployed for detection of location of tube failure.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / alok bhattacharya
When boiler is steaming, only then leak will develop because of steam pressure and faulty tube part. Now in case of heavy tube leakage, boiler must be stopped immediately and maintain drum level in order to avoid starvation and further damage of tubes. Moreover boiler need to be depressurized simultaneously.
Thanks
Is This Answer Correct ? | 0 Yes | 0 No |
Hi,
I am assuming you want to stop the feed water to attend the tube leakage. But it is not clear what the question is about. IF the light up has been done,I do not think the flow of the water in boiler can b stopped. Secondly if light up has not been done then better to shut down the unit and properly take up tube leakage attending procedure.
Is This Answer Correct ? | 0 Yes | 1 No |
What is definition of hydrogen cell?and were are you use?
Why reheater is not used after IP turbine.
What is difference between secondary Air & Tertiary Air and Their use.?
why HT motor star not grounded?
what is under voltage protection 27
What is droop.
2 Answers Dhampur Sugar Mills, Elaf,
why Subcritical has 60% condenser capacity
.What do you mean by Turbine Dump.
1.what is the reason for transformer and lightning arrester blast in 33kv system
1 Answers Afghan Telecom, Integra, Sanghi,
Due to the sensitive earth fault Our Power plant Get Tripped Several Times, It happens in the morning time daily, When temperature rises that means sun rises the earth fault current get lower, in this situation What should I do to get rid of this Problem?
Why high pressure turbines are single flow
Why superheated are started before I'd and rd fan?