In dcs contol valve parameters showing like this












Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me



In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td..

Answer / carl_ellis

Gain, ti and td are PID proportional control tuning terms/constants. PID controllers use PID tuning constants to calculate an output based on the error signal; final control elements (valves) do not do a PID calculation so valves are not involved with gain, ti and td. The controller is typically in the control room, the valve is somewhere out in the process.

A PID controller calculates the expected valve/damper position from the error signal and the tuning constants, the result of which is an output control signal ranging from 0-100%.

A valve positioner or valve I/P receives that control signal from a controller (4-20mA, Profibus) and supplies air or electric power to the actuator to achieve the correct position demanded by the control signal.

Ti is the term for reset or integration. It is used when the process itself is not an integrating process. Level, pressure, and pH are usually integrating processes. Sometimes temperature is an integrating process, sometimes not. When the process is non-self regulating/integrating process, the ti term is not used in the PID calculation.

Flow and temperature processes typically use the ti term for PID calculation.

An exception to the rule of PID being done in a separate controller is Foundation Fieldbus (FF), which allows function block PID execution in FF devices. In a case where PID control is executed in an FF valve positioner, then a valve would use the PID tuning constants.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?

6 Answers   OGDCL,


Anybody can tell me  how to convert mmHg2o /psi to scfm  please give me formula of conversion

0 Answers   Samsung,


what is the approximate cost of U tube manometer having range 1000mmwc to 1000mmwc?

1 Answers  


What is difference between differential pressure & delta pressure?

0 Answers  


Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000

1 Answers  






What is basic of instrumentation

8 Answers  


Why the tapping connections are taking above for gas service and below for liquid service?

4 Answers  


What is surge in compressors? How to detect and control it?

3 Answers   Kharafi National,


whether radar level transmitter is applicable for the open tank

1 Answers   TCL,


what is the function of a zener diode ?

2 Answers   Honeywell,


In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...

6 Answers   L&T,


Why do we have earthing cable in branch cable and shield in the same cable?

0 Answers   Process Control Technologies,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)