For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
Answer / parvez alam
In 440 volts, 3-phase star connected system Vph=Vl/1.732 which is equals to 440/1.732=250V. So Vph is voltage between phase and neutral and Vl is line voltage between two phases. Also power in 3 phase system is 1.732VlIl x power factor.Also Il=Iph
But in delta connected system it is just the opposite of 3 phase system, so we have Vph=Vl because there is no neutral in delta system.Also Iph = Il/1.732
Is This Answer Correct ? | 9 Yes | 0 No |
1. What is differential relay? How it operates?
what is interference
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
What is x/r ratio?
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.
what is IP65 & What is its advantages
Why, the starting current of 3 phase Induction Motor is 7 to 8 times its rated current?
how to give earthing in ships?
What is different between Circuit breaker and Isolater?