Transformer calculation
Answer / faiyaz
We know that, Transformer always rated in kVA. Below are two simple formulas to find the rating of Single phase and Three phase Transformers.
Rating of Single Phase Transformer:
P = V x I.
Rating of a single phase transformer in kVA
kVA= (V x I) / 1000
Rating of a Three Phase Transformer:
P = √3. V x I
Rating of a Three phase transformer in kVA
kVA = (√3. V x I) /1000
but lets me try to explain.
Here is the rating of Transformer is 100kVA.
But Primary Voltages or High Voltages (H.V) is 11000 V = 11kV.
And Primary Current on High Voltage side is 5.25 Amperes.
Also Secondary voltages or Low Voltages (L.V) is 415 Volts
And Secondary Current (Current on Low voltages side) is 139.1 Amperes.
In simple words,
Transformer rating in kVA = 100 kVA
Primary Voltages = 11000 = 11kV
Primary Current = 5.25 A
Secondary Voltages = 415V
Secondary Current = 139.1 Amperes.
Now calculate for the rating of transformer according to
P=V x I (Primary voltage x primary current)
P = 11000V x 5.25A = 57,750 VA = 57.75kVA
Or P = V x I (Secondary voltages x Secondary Current)
P= 415V x 139.1A = 57,726 VA = 57.72kVA
Once again we noticed that the rating of Transformer (on Nameplate) is 100kVA but according to calculation…it comes about 57kVA…
The difference comes due to ignorance of that we used single phase formula instead of three phase formula.
Now try with this formula
P = √3 x V x I
P=√3 Vx I (Primary voltage x primary current)
P =√3 x 11000V x 5.25A = 1.732 x 11000V x 5.25A = 100,025 VA = 100kVA
Or P = √3 x V x I (Secondary voltages x Secondary Current)
P= √3 x 415V x 139.1A = 1.732 x 415V x 139.1A= 99,985 VA = 99.98kVA
Consider the (next) following example.
Voltage (Line to line) = 208 V.
Current (Line Current) = 139 A
Now rating of the three phase transformer
P = √3 x V x I
P = √3 x 208 x 139A = 1.732 x 208 x 139
P = 50077 VA = 50kVA
Is This Answer Correct ? | 4 Yes | 0 No |
What is working of Trip Ckt.Supervision Relay?
Electrical 'C' license full abbreviation , and full form
why a diode bridge is provided in vcb control circuit ?
how much Amp we can put in 1200kva generator?
STATE WORKING OF SF6 C.B.?
Please tell me the earthing procedures adopted for the STAR-STAR 3 Phase transformer in india and give a better sugession for earthing
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
why C T secondary are rating 5A generaly .
How can we estimate Gen rotor current?
if an induction motor is operated at unity power factor what will happen? will motor run or not? kindly describe a logical answer?
what safety use in electrical panel
what is use of governer in diesle engine