Answer / carl_ellis

Disconnect the field sensor.

Connect a calibrated/traceable temperature signal calibrator.

Apply LRV value.

Trim the 4.0mA output.

Apply the URV value.

Trim the 20.0mA output.

Check as many interim points as the calibration protocol requires and note the output and the deviation from the expected value.

Determine whether the transmitter is within spec from the deviation values seen.

If transmitter passes, reconnect the field sensor to the input.

Fill in the paperwork.

Carl Ellis
Measure First

Is This Answer Correct ?    9 Yes 3 No

how to calibrate TT transmitter..

Answer / eid elatawy

First i have to know the connected element
1. RTD :using resistance box and divide the range into 4 quarters for example the range 0 to 100 deg we have 0,25,50,75,100 will find the related resistance from the table and see the transmitter output and if any deviation will make trim zero and span trim.
2. TC the same idea but we use MV supply and by using TC tables.

Is This Answer Correct ?    4 Yes 0 No

how to calibrate TT transmitter..

Answer / karishma

First do span and zero adjustment of a temperature transmitter. Then when the input signal is zero the output is 4mA if not readjust the span and zero again provide 25% 50% 75% 100% Signal and see the output it should give 20 mA for 100% signal input. 

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is diffrence between analog card and digital card in plc.how analog card work,Please explain in detail.Please send it on abhi_vyas@sify.com

6 Answers  


What is SLPC & MLPC? How it works?

2 Answers  


Can we use PLC in Hazardous Area?

2 Answers   MNHG,


Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?

0 Answers  


how many types of sensor in instrumentation

3 Answers   SRACO,






WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.

8 Answers  


In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?

0 Answers   Reliance,


What is cold junction compensation in thermocouples? How is it achieved?

4 Answers   Honeywell,


In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?

0 Answers  


How is plc installing done

3 Answers   L&T,


what is interlock system and why we use of this?

0 Answers  


What are different type of instrument cable

0 Answers   KOC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)