how to calibrate TT transmitter
Answers were Sorted based on User's Feedback
Disconnect the field sensor.
Connect a calibrated/traceable temperature signal calibrator.
Apply LRV value.
Trim the 4.0mA output.
Apply the URV value.
Trim the 20.0mA output.
Check as many interim points as the calibration protocol requires and note the output and the deviation from the expected value.
Determine whether the transmitter is within spec from the deviation values seen.
If transmitter passes, reconnect the field sensor to the input.
Fill in the paperwork.
Carl Ellis
Measure First
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / eid elatawy
First i have to know the connected element
1. RTD :using resistance box and divide the range into 4 quarters for example the range 0 to 100 deg we have 0,25,50,75,100 will find the related resistance from the table and see the transmitter output and if any deviation will make trim zero and span trim.
2. TC the same idea but we use MV supply and by using TC tables.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / karishma
First do span and zero adjustment of a temperature transmitter. Then when the input signal is zero the output is 4mA if not readjust the span and zero again provide 25% 50% 75% 100% Signal and see the output it should give 20 mA for 100% signal input.
Is This Answer Correct ? | 1 Yes | 0 No |
what is diffrence between analog card and digital card in plc.how analog card work,Please explain in detail.Please send it on abhi_vyas@sify.com
What is SLPC & MLPC? How it works?
Can we use PLC in Hazardous Area?
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
how many types of sensor in instrumentation
WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.
In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?
What is cold junction compensation in thermocouples? How is it achieved?
In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?
How is plc installing done
what is interlock system and why we use of this?
What are different type of instrument cable