Answer / joseph
You can connect Single Phase capacitors to individual
phases. Alternatively you can use three phase capacitor
unit directly. Another option is to use Single phase
capacitors rated for 415 or 440V, make a delta connection,
and connect in three phase.
Is This Answer Correct ? | 35 Yes | 4 No |
Answer / rai hasnain
in single phase circuit capacitor use in parallel the circuit
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / sheikh
Commonly in industries there are used mostly three phase load like motors. transformers e.t.c utilized 3 phase static capacitors which internally made star or delta connection
rating of capacitor denoted in KVAR LIKE 50 KVAR, 25 KVAR and others.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / h r rajyaguru
In three phase load the capacitor bank is connected for improving the power factor (P F). The rating (KVA and V) of the bank can be calculated depending on the existing system voltage and up to which P F we intend to improve. The ideal location of this Capacitor Bank is near to the load. For large size motor / load separate circuit breakers are to be used for switching the said Capacitor Bank. The motor and the bank are to be closed / opened simultaneously. Some times Capacitor Banks are connected with the Motor Control Center (MCC) or Power Control Center (PCC) for improving the P F of the system. The voltage rating shall be 10% higher than the system voltage.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / venkatesha sharma
star or delta connected bank interfaced between three
phases.
Is This Answer Correct ? | 5 Yes | 3 No |
In low voltage system we put capacitor bank in parallel to the PCC (POWER CONTROL CENTER) in that bank capacitors having delta connection.On HT bus series capacitor bank is used.Induction motor having long cable distance we use capacitor bank in delta connection.In large high voltage motor having large rating use capacitors bank along with reactor.
Is This Answer Correct ? | 1 Yes | 0 No |
A delta-connected bank of capacitors is usually applied to voltage classes of 2400 volts or less. In a three-phase system, to supply the same reactive power, the star connection requires a capacitor with a capacitance three times higher than the delta connected capacitor.
Capacitors shall be connected near to the load.Some times Capacitor Banks are connected with the Motor Control Center (MCC) or Power Control Center (PCC) for improving the P F of the system. The voltage rating shall be 10% higher than the system voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the ckt diagram of a tubelight and is it the simplest ckt of electrical engineering and also the component?
What types of question are done for diploma students in aptitude test
WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?
What are the various reasons for an inductin motor to get heated?
what are the types of 3-ph. generator protection
What is polar plot?
How npn and pnp transistor works
Stator of 3-phase IM has 3 slots per pole per phase. If supply frequency is 50 Hz, calculate the speed of rotating stator flux A 1000 rpm B 500 rpm C 1500 rpm D 1440 rpm
what is V0/V rating of cable
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
Is Indian railway uses 25000v ac or dc?