HOw To Use 24V DC in Instrument?
Answers were Sorted based on User's Feedback
Answer / k. ksharma
All electronic device are operated to 24volt DC supply. Two terminal positive and negative, negative wire comman for each loop.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
24Vdc is the DC power supply voltage.
For 2 wire loop powered instruments, the DC power supply is
in series in the loop.
For 3 wire instruments, the DC power supply common (-)
shares a terminal with the receiver's common (-),
but has a separate (+) terminal.
For 4 wire instruments, there separate wiring terminals for
both the power supply (+) and (-).
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
Why does a pressure gauge installed on reactor, doesn't have any vent line below to release the pressure? Is it any kind of designing mistake or it actually does not require any vent line? And if it does not require any vent line below it then how we are gonna release the pressure built inside the pressure gauge?
0 Answers Process Control Technologies,
How to regulate the flow of Air in 4" line, with max flow of 330 nm3/hr and Pressure of 0.5 bar? please suggest the type of instrument required.
how many type conductivity sensor ?
Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????
4 Answers Aramco, Asian Paints,
what is flow equation of kg/hr to m3/hr
Why would an Engineer consider combining FEEDBACK and FEEDFORWARD control in some applications?
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
Before erect the instrument what should you do?
why I need valve guard and whats different between guard and positioner ??
Explain pH, Conductivity.
difference between repeatability and reproductability
principle of dead weight tester ?