A 200 KVA UPS's load current is 70 A. We want to provide a
Generator back up. What capacity of DG required for this ?
Answer / laxmikant
Question is not clear,
Because 200kVA/(1.732x0.415kv)= 278.24 Amps/phase.
Please check. If you load demmand is 200kVA , as DG runs
always with 89% efficiency @ 100% load, You may choose for
250kVA DG.
| Is This Answer Correct ? | 2 Yes | 0 No |
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
how to calculate mf when meter and cTPT detail are given
Why we use Delta connection in the secondary side of a High Voltage transformer?
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
What is basic impulse insulation level? And how it is calculated for sub- station?
What is the difference between IGBT and TRIAC?
what is difference between KW and KVA
how can we connect the capacitor bank to improve the power factor?
How many turns are there in primary winding? (In Transformer)
what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)
will a fluorescent bulb work when dc is passed through it?? if not why??
Swg formulae
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)