WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT?
1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE.
2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100%
OUTPUT.
3)LINEARITY PRBS.
4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
Answer / carl_ellis
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT?
1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE.
2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100%
OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO
POINT IS WRONG.
The correct answer is 2, but number 4 also requires a span
correction.
1) The "Zero-point and 100% are correct, but not a
mid-range value" problem is a linearity problem.
2) The "Zero-point is correct, but 100% input is not giving
100% output" is a span problem.
4) The "100% output is correct but zero point is wrong" is
a zero offset AND a span problem because when the zero point
is corrected with the addition of a bias/offset, the 100%
point will shift up or down the same amount as the zero
shifted with the bias/offset correction. So the 100% point
will no longer be correct once the zero is corrected.
Hence, the zero AND the span will need to be corrected.
Carl Ellis
Measure First
| Is This Answer Correct ? | 8 Yes | 2 No |
how radio frequency level probes works with its controller ? what is its principle ? pls give me brief explanation?
what is easiest way to read STL language in PLC?
how to calculate the total flow in square root
how to explain PID?
what is the procedure for auto tune in masoneialn 12300 series displacer type transmitter?
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).
why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?
What is Droop? What is Step/Gradient Limiter in Turbine Governor control?
Somebody tell me in what way i need to prepare for csio pgrpe(adv instrum eng)interview?what all the quest can i expect?
Do you have reference list?
what does ip65 signify??what is its NEMA equivalent???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)