can we use ACB for HT supply
Answers were Sorted based on User's Feedback
Answer / sheikh
I think ACB rated voltage is not more than 600V AC thereby
ACB cannot used in HT
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jagsagar@rediffmail.com
ACB's are capable only upto 1000v. HT rating starts from 11KV,22KV.....132KV. Not possiblt to use ACB for HT.
Is This Answer Correct ? | 0 Yes | 0 No |
A cylindrical wire is compressed in length by 10%. The percentage decrease in the resistance will be?????
What are the applications that use Solid State Drives in your home?
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
what are the main parts of DG? explian thier functions?
8 Answers Apollo Power, Tata DoCoMo, Tyco, Vizag Steel,
In a power conditoining unit (inverter) of a solar plant when we measure the d.c. current fed by different strings of solar plates to inverter, the current in the negative wire is less almost by 1 ampere to the current in its positive wire say current in positive wire 5 A , then current in negative wire of the same string is 4 A. Since the current entering should be equal to current leaving then why the current is noticably less in negative wire.
Is C.T will sense the current in both direction. As i know the C.T will sense the current in only one direction.
Why Closing coli supervision is not required for Circuit breaker.
what is the transformer efficiency?
Could u pls tell me the NPCIL electrical engineering interview questions for Executive trainee, and also guide me how to face the interview.
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
in three phase circuit neutral failure what happend in homes