Stepwise process of Northern grid failure in 2012!? (dont
copy paste from wikipedia)
Answer / mebin g mathew
According to the report, Some of the high voltage lines of
Northern Grid were under maintenance and hence the other
lines were highly loaded EVEN 400kv line was used to
compensate the power shutdown of 765 KV LINE. So the 400 KV
line was highly loaded. Due to this the, line tripped and
this worsened the condition load bearing problem for the
other line since all the power requirement came to other
lines. They also started tripping in power swing and some
relays even detected zone 3 tripping(false tripping).
When a huge load was released, the power plant had to shut
them down to protect the generators and other equipments in
plant. A power plant require hours to reignite and start the
production in full flex. And there was a panic to
immediately start production because all were shocked of
the incident.
So thus the norther grid was isolated from other region
grid. That led to a complete black out in North India.The
report ends with an interesting statement that this might
have happened due to hacking of powergrids PLC engineering PC.
Is This Answer Correct ? | 3 Yes | 1 No |
Please give the formula for converting from 1 tr refrigeration to kw.
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
What is the minimum value required for Neutral to Earth in UPS Panels
what is the use of providing earthing for tanks? i know for lightning we use earthing ? Here one of my ONGC project there is no need of lightning protection and there is no power connection near by tank in that situation also ONGC asking earthing for tanks but we didn't understanding why they asking earthing? is anybody tell exact answer?
why we are maintain phase to phase clearence
how can i improve the power factor in domestic (230v)
why generator is star connected ?
What are the main parts of VCB?
what is the difference between HV and LV Breakers?
4 Answers GM General Motors, OEG,
what is power factor ?