what is the ka rating of mccb.
and how it is decided .
Answers were Sorted based on User's Feedback
Answer / aditya shirbavikar
The rating of any circuit breaker is decided on the basis of its breaking capacity. so, the KA rating of MCCB is the unsymmetrical breaking capacity for a particular time.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s.lenin
The KA Rating of MCCB is Defined as maximum current flowing
through the conductor or with standing capacity of the
breaker.the KA is decided mostly that incoming transformer
fault current
| Is This Answer Correct ? | 1 Yes | 0 No |
The value of the kA rating determines how much current the circuit breaker can withstand under fault conditions. The circuit breaker only has to withstand this for a brief period of time, usually the time it takes for the circuit breaker to trip. For example, a value of 6kA means that the circuit breaker can withstand 6,000 amps of current during the brief time it takes to trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT IS THE COOLANTS IN TRANSFORMER?
why do we carry out winding resistance test?
0 Answers MahaGenco, MAHINDRA,
why should small green grass ans small plant should not be there inside the transformer Yard in the factories
differance b|w ground, neutral&earth
what the is the distance between 110kv termination point and the ground. how to calculate
Can I use star delta connected induction motor for dual supply voltage?
Transformer cores are laminated in order to A simplify its construction B minimize eddy current loss C reduce cost D reduce hysterisis loss
Whether it is possible to measure energy at the input of rectifier transformer (12 pulse with very high odd harmonics)
an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly
What is resistance of 50meters, 16sq.mm, single core copper cable?
Why capacitor bank does not require in DG Set?
how to calculate the over current rating of 3phase motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)