Answer / ramakrishna
Losses in transformer cuper losses & iron losses.cuper
losses depends on current iron losses depends on voltagge.
total losses depends on va not depend on phase angle b/w
voltage & current
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / sarbudeen
all the devices (execpt loads like
motor) diesel generators,
transformers, ups are rated in kva
only,
it saying that i can provide total
power (kva) and its ur problem
how u split it (kw+kvar)
depending on load u provided. But
i can give this amount of total
power (kva).
Is This Answer Correct ? | 4 Yes | 2 No |
Because the only thing which doesn't change both side is multiplication of voltage and current. So if any one can calculate the other side values if he have n1 : n2 ratio and any 1 value, ie voltage or current.
Is This Answer Correct ? | 0 Yes | 0 No |
A power transformer contains two main part –the windings-
copper or aluminum conductors insulated –and the magnetic
core.
Magnetic core requires an excitation current in order to
maintain the required magnetic field.
The excitation current depends on supplied voltage and if
the supplied voltage is over a certain limit the excitation
current presents a threshold and start to be very high.
This voltage is the rated voltage.
On the other hand, the conductor insulation rated
temperature is limited-according to insulation class-since
above this limit the insulation will be damaged.
The temperature arise depends of the current passing
through conductor and producing heat losses. These losses
depend only on the absolute value of the current and it is
not connected to the active load [kw=volt*current*p.f. then
the maximum kw it is when p.f.=1 then kw=kVA].
The product of voltage with current is measured in VA or
kVA=1000 VA or MVA=1000000 VA.
Is This Answer Correct ? | 1 Yes | 3 No |
As the transformer is not specified for a particular power
i.e active power or reactive power and the unit of acive
power KW and the unit of reactive power is KVAR for that
reason transformer rating is represent in KVA.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / lokanna.adekar
Losses of transformer depends upon voltage
Is This Answer Correct ? | 0 Yes | 2 No |
What is Hi-Pot Test for Grid Station HV Equipments?
which type of insulation are used on 132kv transmission line
What will be the diameter of pipe between conservation tank and transformer
why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abnormality.
what happens when one of the phases out 0f 3 phases been removed under working condition and no load condition will the machine run if so plz send me why
State the frequency for rc phase shift oscillator?
What is difference between ON delay and OFF Delay Timer?
What is TR of AC?
Classical power system stability was mainly focussed on rotor angle stability but modern power system stability has more focus on voltage stability.Why?
how works inductive &capacitive sensors?
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u
In Round type three phase transformer why the LV side is inner part and HV outer part in the design of transformer? why they cant be opposite?