how to calculate size of cable from motor current given and
how to calculate full load current of a induction motor.
Answers were Sorted based on User's Feedback
First the simple one: IM Full Load Current
I=W/root(3)*V(L-L)*PF*Efficiency of Motor
PF and Efficiency will be available from name plate data of
IM. In general u can consider PF=0.8 and Efficiency=0.85
Ex: FLC of 37 KW motor having 415V, 0.8 pf and efficiency as
0.85
I= 37000/Root(3)*1.732*0.8*0.85
I=75A
For calculating the cable size they are many factors to be
considered
* Load Current
* Voltage Level
* Length
* Voltage Drop
* Temperature Factor
* Grouping Factor
Is This Answer Correct ? | 5 Yes | 2 No |
For further clarification pl mail me @ raviteja.vaka@gmail.com
Is This Answer Correct ? | 4 Yes | 1 No |
the resistance of wire having length X M is R OHEM if i streched the wire to dubble length what will be the resitance
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
In case of legging current of 20°, pf is .94 and leading of 20°,pf is .94 , in mathematicaly both are same but in realy how it is differ ?
Electrical Diagram of Electric Arc Furance from transformer to Furances
can HT cable or HT bare conductor used for LT line? is yes what would be the current rating?
what are the method of testing of transformer??
Power systems
what is the difference between electrical & electronics?
What is mean by CT Saturate? how do we calculate?
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
Why to keep capacitor bank off while generator running.
what is the order of mgnetiation current in a current transformer of 1000A/1A ratio?