Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrutyunjay
Dear Sudhakar Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault) as per IS 3043
Is this equation to be taken for all types of electrodes ( Plate, Rod or Pipe & Strip ) ?
Because , as per IS 3043, same equation is appropriate for plate electrode
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar.g
The earth resistance of single rod or pipe electrode is calculated as per IS 3040:
R=100xρ/2×3.14xL (loge(4xL/d))
Where:
ρ = Resistivity of soil (Ω meter),
L = Length of electrode (cm),
D = Diameter of electrode (cm)
Example:
Calculate number of CI earthing pipe of 100mm diameter, 3 meter length. System has fault current 50KA for 1 sec and soil resistivity is 72.44 Ω-Meters.
Current Density At The Surface of Earth Electrode (As per IS 3043):
• Max. allowable current density I = 7.57×1000/(√ρxt) A/m2
• Max. allowable current density = 7.57×1000/(√72.44X1) = 889.419 A/m2
• Surface area of one 100mm dia. 3 meter Pipe = 2 x 3.14 x r x L = 2 x 3.14 x 0.05 x3 = 0.942 m2
• Max. current dissipated by one Earthing Pipe = Current Density x Surface area of electrode
• Max. current dissipated by one earthing pipe = 889.419x 0.942 = 837.83 A say 838 Amps
• Number of earthing pipe required = Fault Current / Max.current dissipated by one earthing pipe.
• Number of earthing pipe required = 50000/838 = 59.66 Say 60 No’s.
• Total number of earthing pipe required = 60 No’s.
• Resistance of earthing pipe (isolated) R = 100xρ/2×3.14xLx(loge (4XL/d))
• Resistance of earthing pipe (isolated) R = 100×72.44 /2×3.14x300x(loge (4X300/10)) = 7.99 Ω/Pipe
• Overall resistance of 60 no of earthing pipe = 7.99/60 = 0.133 Ω.
If you have any doubt regarding this ...pls mail me sudhakar28485@gmail.com
Is This Answer Correct ? | 4 Yes | 5 No |
what are the different types and applications of compressors?
how to calculate efficiency of voltage and current controlled welding transformer?
draw the block diagram of fire alarm?
why lightning arrester and other equipment earthing conneting from same earth bar ?
what is AVR? what is the function of AVR?
In a 3 phase induction motor(without connecting supply) if we rotate its rotor by hand and check resistance of stator winding at motor terminal box its resistance varies why ??
transformer core are laminated for what purpose?
ho w to make Incident and accident reporting
In Plug used in house,Why Earth of the plug more thicker & deeper?
I need bhel electrical test pattern & paper
What is meant by transformer, why it should be used, with out that equipment what happens if we transformed the supply?
What is resonant peak?