Dear Sir / Madam,
Actually we requied 64 A MCB,
But i have 32 A MCB = 2 No's
this two i have to make series connection and we usw any
place?
isit possible or not......
Answers were Sorted based on User's Feedback
Answer / sagar
NO.
Because
MCB is used for over current protection.
you require 64A MCB for protection.
now if you will use 2 MCB of 32 A , then both the MCB will give protection for 32 A and will trip at 32 A.
so , you can't use the 32 A MCB in place of 64A MCB
Is This Answer Correct ? | 21 Yes | 1 No |
Answer / hemant
if u connect 2 mcb's in series then it share load up to 32
amp only not for 64amp. if u used this two mcb then u must
to divided load in to two section like 32/32 amp. after
then u can connect load to out going terminals of mcbs.
Is This Answer Correct ? | 14 Yes | 0 No |
you can do that, but in parallel. not in series
Is This Answer Correct ? | 3 Yes | 0 No |
MCB USE ONLY LOW TENSON THIS RANGE 6AMP. TO 63 AMP.
VCB USE ONLY HIGH TENSON LINE FROM 2000AMP TO 4300 AMP.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the reason for harmonics introduced in the line
What should be the minimum depth of ground laid 66 kv ht cable?
Differentiate between low pass, high pass and band pass filter?
How many types of colling system it trformers?
why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.
In motors how many types of cooling systems were used?
why current flow throgh conductor.
When semiconductor fuse does save thyristor in each cycle of conduction? Why under voltage setting keep less in SPRS and more in DC drive?
the question is about buchloz relay why we called it buchloz relay
Plugging is a phenomenon to= A braking the motor B to accelerate the motor C to run IM as generator D to start the motor
how CBCT works?
why excitor coil of an alternator can fail