Answer / guest
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / prasad damodar bhoir
kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / h salim
Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8
Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prakash g.r.
Calculation of Required Kvar
Initial or Present Power Factor =Qi,
Required Power Factor = Qd
KVAr= KW(TANQi-TANQd)
Qi=COS-1PFi = Initial Power Factor Angle
Qd=COS-1PFd = Final Power Factor Angle
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ahatesham
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 2 Yes | 0 No |
Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]
| Is This Answer Correct ? | 0 Yes | 0 No |
How we calculate the size of ht cable for any transformer
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
what is stator inter turn fault?
What is difference between Electrical & Electronic Device?
7 Answers AZ Engineering, Vodafone,
How to checking sld drawingas and control drawings
What is application/Function of Electro chlorinator in Offshore Oil & gas Platform ?
Q: How to calculate Transformer losses , tell us by Formula.
What is a roll of a adopter pannel in buscoupler pannel????
Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce
why generator and t/f ratings given in kva?
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
i want use the cable size 16cx4 core aluminium usege watts 240x2000w this cable size is correct?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)