why transformer calling in VA rating
Answers were Sorted based on User's Feedback
Answer / murali290
For any device the rating is given based on the losses occur
in it (loss is nothing but heat).In transformer 2 types of
losses occur 1.core losses: which depends on V &
2.cu losses: which depends on I only
but no losses depends on p.f.
therefore trasformer rating proportional to VI or VA
for large transformers the rating in kilo or mega ,hence
KVA or MVA
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / praha tuty
Transformer has copper loss & iron loss. copper loss occur
in windings & it is due to emf.Iron loss occur in core due
to current. so in order to measure the both losses,
transformer ratings are in VA rating.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / rakesh maharjan
The KW rating is dependent on the power factor and power factor can be different depending the condition where as mostly 0.8, but if KVA rating is given we can calculate the KW rating as per our condition. So KVA rating is fixed and reliable to any malfunciton not to occur. so the transformer rating is given in KVA.
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / pramod attri
it's using step up, and step down at same frequency..by
mutual inductance.. it case transformer calling in kv,,,
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rajeshambur
transformer have a two losses because open circut and short circut . two losses so transformer rating in va
| Is This Answer Correct ? | 1 Yes | 11 No |
why we can turn on the phase-A scr in 3 phase converter at 30 degrees
how to select a breaker (MCB,MCCB,ELCB) for 18.5 kw, 3 ph. 480 v, 60 hz induction motor?
wat is meant by PX class in ct?
if ELCB and RCCB connected in series,what wiil be the result
the cheapest inducting instrument among all is a)pmmc b)moving iron c)electrodynamometer d)rectifier
What is difference between start imitation and start interlock for 3 phase motor protection ?
what is difference between neutral& grounding?
what solid earthing means?
Difference between transmission line and cable?when ever a large water channel has to crossed it is easier to use cable then transmission line why?
in the exciter the power is feeded from battry or control or whatever.and we need it in the generators for the stating . do we need it in the shutdown also?i mean the exciter>
What is the differemce between Pulse transformer and Welding transformer.
Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)