Answer / loganathan
Yes we can measure pressure with the help of Differential pressure transmitter,we have to connect the HP side of the transmitter to the process line where we are going to measure the pressure,But only thing is we can measure only up to the range of minimum since Differential pressure transmitter will be in range om mmwc.
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / manishahir
we measure pressure using differential pressure transmitter by connect the HP side of the transmitter to the process line and LP side of transmitter should be open in atmospheric.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / dhiru patel
Yes,we can use DP tx for pressure measurement for vacuume pressure(absolute PT) and low gauge pressure measurement.It depends on service,pressure range and diaphragm material.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
we know that dp transmitter working principle on pressure difference and in dp type transmitter two ranges URV and LRV
1 LRV is low side value and 2 URV is high side value
SO only reed high side pressure this is vessel pressure
or connect the hart comminucator and then display the vessel pressure
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / johnan
actually we can use the differential pressure transmitter to measure the flow and level, not the pressure, how, if level, it calculate the difference of high side and low side of the transmitter, then it convert to the level using formula,it is a very long explanation,this is only a laymans term...
Is This Answer Correct ? | 0 Yes | 9 No |
What is cavitation. what is the effect of it on control valve and how is it prevented.
How to calibration a control valve?
give some question relative instrument fitter?
if found error in magnetic flow meter?how can we adjust?
2 Answers ANI Instruments, Techint,
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
Determine the manipulated variable, controlled variable, and the measured variable given a description of various typical industrial processes.
what is HVAC?
I want to take temp. data from recorder to computer. Which communication system is best from this option(Rs 232- 485/ethernet/USB)?
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?
why we use negative 24vdc to a proximeter
What is the load line in control valve?