i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
Answers were Sorted based on User's Feedback
Answer / raj
Open tank level calculation = tank hight * density
Example for
3 meter tank hight
Process liquid for disel density 0.7
So calculation
3 * 0.7
2.1 meter
LRV. O
URU 2.1 meter if you wand change to mmh2o the unite
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / nitin sompura
See as per your data open tank height is 2.5 mtr
(2500mm).zero and 100% level if we consider as per your
tank and we suppose no safety margin for overflow as well
as for zero level for the pump, as you have not mentioned
clearly,
so according to you please keep your LP of DPT in
atmosphere, and HP point connect to the bottom of tank,and
if we consider tank of water then LRV:0.0mmWC,URL:2500 mmwc.
as per your medium you consider density.
Is This Answer Correct ? | 7 Yes | 1 No |
why we are using orfice plate? then difference between orfice 7 nozzle plate?
1 Answers Flour Tech Engineers (P) Ltd,
How many are the types of instrument cables in terms of No. of pair.
what is ment by PID controllers? explain with example?
Why we are using temperature and pressure as a reference when measuring flow of steam?
How to interfacing microcontroller with a DC motor
how to trim the pressure transmitter ?
How many interlocks at turbine side?
how to calculate density?
If fire would be inside the plant which fire detector is to detected the fire.
what is the different between plc and dcs ? I know full name of this two but I want to know what structure and working style and speed I/O capacity and controller difference?
what is plc? Basic function of plc? application of plc in industry? What is lader diagram ? What is the main advantage to use plc in industry?
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)