How Can we calculate the rating of a cable?Show the formula?
Answers were Sorted based on User's Feedback
Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
| Is This Answer Correct ? | 0 Yes | 1 No |
what is power factor ? why is it so important?
how can see the ac indoor or out door ac which Tr
What are armoured cables?
What are the types of windings according to the construction?
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
what is the location of lighting switch of battery room
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
Sir Power transformer :- (in generating station) Alternator terminals side - Delta HT transmission line side - Star Why?
IS there any mechanical connection between the field winding and armature winding of a dc generator?
what is the dedicated earthing
what is the difference between arc and spark
What is meant by IP55 motor.Where it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)