I have flow transmiter DP range is 0 to
5000mmwc,(convert) Display to be show in
m3/Hr.
Answers were Sorted based on User's Feedback
Answer / sajid ali khan
Dear the Flow range is not just a function of the flow
transmitter. It is function of the Flow Element, that can
be an Orifice or a venturi, etc.
You have to know the Flow calculations and then calculate
the relationship of dp vs flow
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sivaram
Dear bro.In flow calculation Need Design DP and Q Parameters,Then configure range DP ,out put function Sq root display range configure Given Q,Simple you will get Exact
flow
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kirubakaran
example:
50% range =squareroot of(d.p/max-min)
50/100 = square root of(dp/5000-0)
take square on both side
2500*5000/10000= d.p(differential pressure)
1250mmwc= d.p
similiarly find 0%,25%,75%,100% this is for square root output
pls see range in dcs example 0-50ton
then put corresponding value
range o/p(ma) mmwc tons
0% 4 0 0
25% 8 312.5 12.5
50% 12 1250 25
75% 16 2812.5 37.5
100% 20 5000 50
if u feel correct means follow this
| Is This Answer Correct ? | 3 Yes | 6 No |
Before erect the instrument what should you do?
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
What is the cv of a control valve?
Hi, I am Newely Joined in Construction company instrument engineer? Any one can Plz tell me How can I advanced preparation for Releated Engineering and construction Documents?
What are the application of bernoulli’s theorem?
A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?
When can a bypass not used on a positioner?
what is the basic principal of vertax flow meter
3 Answers Balrampur Chini Mill, Saba,
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
what is function of ESD , and how is it work, explain with difination
1 Answers Bapco Bahrain Petroleum Company, BMB,
Give me best instrumentation Books name..Ple...
can a control valve works without positioner?why need tunning of c/v?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)