Q. calculate the value of the resistor to be connected in series with a 100W;
230V lamp so that the wattage of the lamp is reduced to 35W
Answers were Sorted based on User's Feedback
Answer / 230
power = 100 W,= VI
volts = 230v,
I=V/P;
I=100/230;
=0.4347;
R=V/I;
=230/0.4347;
I=529.1,
NEXT POWER REDUCED TO 35 MEANS, 2.8* R;
=2.85*529.1;
=1507.9 Ohms.
That is 1507.9 Ohms to be increased to get 35 W
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sagar
power P =VI
I = 100/230 = 0.4347A
when there is no addition resistance connectedt,then
R = V/I = 230/0.4347 =529 ohm.
If we want to reduce power to 35 w ,then
I = 35/230 = 0.1521A should be flow
for that value of resistance
R = V/I = 230/0.1521
=1512 ohm.
so,series resistance conneced will be,
= 1512 - 529
= 982 ohm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / gmpk
dear friend,where is the series resistor in the circuit.
the actual question that what is the resistance between
source and load if the load is 35w instead of 100w.
100/35 is 2.8 times has reduced. so if we multiply the actual
value of resistance will come
| Is This Answer Correct ? | 1 Yes | 0 No |
lamp 100W/230v
when resistor R is connected in series with the lamp.
lamp power=35W
lamp Voltage= 230V /* since 230v is the operating voltage of the lamp*/
series current = 35/230
=0.152 A
power dissipated at a resistor = 100 W -35 W
= 65 W
= Isqr X R
R= 65/(0.152sqr)
= 2.8 kilo-ohm
| Is This Answer Correct ? | 0 Yes | 0 No |
what is fuction static switch in ups and tell me use parts name and fucion
What will happened if the neutral of the (star connected secondry) Xformer disconnected? (if its Above KVA rated one)
can u guys pls suggest a good material for learning abt switch yard and its components
in 5 mva transformer 33/11 kv s/s what rating of capacitor bank is required & what is the fourmula for rating
I have 2 KW electric water heater.I am gonna use it in controlling water temp.so I needed to increase or decrease the heating capacity.is there any electrical-electronic circuit for varying the resistance & so current?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
Types of 132KV and 222 KV protection.
what happens when series resonance occurs?
how to caculate cable size for diff types of loads? if anyone know the calculating procedure please tell me
what is the difference between LATCH and FLIP FLOP
why hv current transformers have big size ?
What is kirchoff ’s current law (kcl)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)