How we will check whether the proximity, which we have is
either NPN or PNP, if no data sheet or manual or any
details is available to us ???
Often identification data is printed on proximity (or prox) sensor's label but it is not uncommon for the label to damaged, missing or unreadable.
Many prox sensors are DC powered, 3 wire devices that conform to a standard wiring color code:
brown is (+) supply voltage, typically 24Vdc
blue is (-) supply voltage common or return
black is the sensor's switched output
To test a 3 wire sensor to determine whether it is a PNP or NPN type you need a DC power supply and a DC voltmeter.
Set the meter to DC voltage to a range greater than the supply voltage (typically 24Vdc), like 50/100/200/600V
The black meter probe should be in the 'common' meter socket
The red meter probe should be in the DC 'volts' socket
Connect the sensor's brown wire to the power supply (+)
Connect the sensor's blue wire to the power supply (-).
Turn the power supply on.
Ensure that the prox sensor is not triggered by presence to an object.
Connect the black meter probe to the blue sensor wire.
Connect the red meter probe to the black switched signal output sensor wire.
If the meter is connected to a PNP device, the meter will read 0V.
If the meter is connected to an NPN device, the meter will read 24Vdc.
Force the sensor to change state/output by detecting an object.
- If it is an inductive proximity switch, place a piece of metal in front of the sensor.
- If it is a photoelectric sensor, block the photoelectric beam.
- For an ultrasonic sensor or a capacitive sensor, you can just use your hand to make the sensor output. Some prox sensors use an LED that lights up when the sensor detects an object.
With an object present, a PNP device's output will change and the voltmeter readout will read 10V to 30V. This is also known as a "sourcing" device.
With an object present, an NPN device's output will change and the voltmeter readout will be 0V. This is also known as "sinking."
Another test to check for PNP:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.
When sensing no object, the signal output will be 10V to 30V.
When sensing an object, the signal output will be 0V.
Another test to check for NPN:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.
When sensing no object, the signal output will be 0V.
When sensing an object, the signal output will be 10V to 30V.
| Is This Answer Correct ? | 3 Yes | 0 No |
HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY IT IS USED ON ESD ON OFF VALVES?
What is SCADA ? WHAT is it role in DCS ?
how the actually positioner of control valve working? where we gave 3-15psi pressure to I/P converter where it is firstly applied ?- on I/P to positioner then what happen? is control valve operate on 3-15 psi or its bench pressure?
line up procedure for dp type flow transmitter?
Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.
Can u tell me the principle of the tc,rtd,level switch,pressure switch ,transmitter(pr flow level temp.),vibration...plz
what is the difference b/w normal thermocouple and skin type thermocouple?
What is the start up procedure of desalter
How to calculate 47Liter H2 Gas cyilnder consumtion? Cylinder inlet Pressure is 200bar and Discharge pressure is 6.0bar. Flow is 100ml/min.For the above condition how many days one cylinder can be used?
WHAT IS THE MAIN WORKING OF BOILER.
TEMPERATURE VARIATION FOR FREQUENTLY.
1 bar is equal to how many pound per square inch(psi)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)