Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
| Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
| Is This Answer Correct ? | 3 Yes | 3 No |
I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?
May I have a brief note above the voltage barriers? Whats is the purpose? Please mail me if you've operational details, mail id: rajkumar.diice@gmail.com
How to check range of DP Transmitter
What inherent design and operating principles are included in a modern control system to use predictive maintenance practices to increase overall system reliability?
what is the difference between attemperator and desuperheater ?
how the presure switches are calibrated? and what happen inside?
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
why two probes are used in turbine flowmeters?
Tell about your IFFCO plant visit.
why are use only 4 to 20ma. signal.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)