YOU NEED A CURRENT TRANSDUCER AT YOUR MCC WHICH CAN GIVE YOU
THE 4-20mA SIGNAL WITH 0 TO 70Amps. proportionally.
USE LESS THAN & GREATER THAN BLOCK LOGIC FOR OPEN & CLOSE
THE VALVE.
Is This Answer Correct ? | 7 Yes | 0 No |
U dont need any plc logic for such application since u can
do this project with the help of simple transducer which
will gives the mA o/p with respect to ur Amps. & just i/p
converter which will help u to open ur positioner valve.
Is This Answer Correct ? | 5 Yes | 0 No |
dear sir we have insatlled positioner model no.sipart PS2 make Siemens at our control valves . now problem is if we want to increase the response of valve opening speedy /fast. what parameters do we change for positioner ? any idea. please guide us.
What is the basic principle of vibration measurement by BENTLY NEVADA vibration measurement system? and Why it gives the -ve voltage output?
14 Answers Ensol, GNFC, Reliance, Siemens,
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
units of pressure,flow, level,temperature? principle of pressure gauge? calibration of pressure tx., level tx., temperature tx.flow tx.? description of two wire ,three wire and four wire R.T.D.? WHAT IS INPUT AND OUTPUT OF TX.? WHAT IS INPUT AND OUTPUT OF R.T.D. AND THERMOCOUPLE? WHAT IS HOT LOOP AND COLD LOOP? WHAT IS INPUT AND OUT PUT AND OUTPUT OF D.C.S. AND P.L.C.? PRINCIPLE AND WORKING OF HART? WHAT IS PNP AND NPN PROXY? CALIBRATION OF PRESSURE ,LEVEL ,FLOW SWITCH? DESCRIPTION OF FIELDBUS FOUNDATION? WORKING OF SOV.?
what is the responsibility of an instrument commissioning supervisor
what is dead weight tester and where it is used?.
11 Answers DuPont, Jain steels,
what is cavitation in control valve? & how we can avoid it?
1 Answers Forbes Marshall, Reliance,
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
the basic of a DP flow transmitter are the following
can you suggest good traning institute in instrumentation ? (in automation, or designing)
why pneumatic control signal output is use 0.2 to 1 kg/cm2
How to calibrate Toxic gas detector?