Answer / kathirvelan.j
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52 Amps
But we need to consider the safety margin of atleast 125%
on the MCB rating and also there are only standard current
ratings are only available in the market so by considering
all these reason we can go for a 65Amps DC MCB.
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / asif.k64@hotmail.com
UPS is 10 KVA, and battery is 65AH
Hence if it is a 1 phase UPS
KVA = V*A
10000 = 240*A
A= 10000/240
A = 42 A full load
Approximately a 63 A MCB would be required
Is This Answer Correct ? | 21 Yes | 7 No |
Answer / ravi v nair
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52.08
we need a 55A DC MCB
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / naveen kumar.b
Ans:- 60Amps MCB
how:-
for 16 battery net voltage is 192Vdc.
For battery low cut OFF voltage fixed in by all kind of ups is 10.5 each battery . so for 16 battery System battery low cut of votage is 168VDC
( :- at time low battery voltage only Dc current consumption is high, we need to take maximum current consumtion for select MCB)
total load we taken= 1oKVA Full load.
DC voltage at time low battery = 168
current consume (at time of low batter)= 10000KVA /168Vdc
current consumption is 60Amps arround
so 60Amps MCB is required
Is This Answer Correct ? | 2 Yes | 0 No |
What are the precautions to be taken before working on a cable?
i seen a 132kv/11kv transformer,and thier is a sugar factorys 10MW EXPORT PLANT,MY QUESTION IS THAT WHEN THEY EXPORT ELECTRICITY THEY USE THE SAME TRANSFORMER AND THE CONNECT IT TO 132/11KV TRANSFORMERS SECONDARY SIDE CAN ANY ONE EXPLAIN IT.. THE TRANSFORMER IS OF KIRLOSKAR MAKE AND IT HAS TAP CHANGER.
If We are converting the SINGLE PHASE AC into THREE PHASE AC by using STATIC CONVERTERS , then How do we bring the frequency to 50 hz??
what is meant by reactive power ,active power & real power ? thank you
The 3 phase Delta connection RB=440V, BY=350V,.......* is Line to Line voltage RY= ? And Formula....?
ho w to make Incident and accident reporting
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
what is the principal of braker
what is the difference between EMF and potential difference??
what use marshalling kishock in power transformer?
How to select HT/MV cable size ?