1 HP = how many Kva
Answers were Sorted based on User's Feedback
Answer / surya
1 HP=0.746KW. Assuming the PF ia 0.8, then 1 HP= 0.746/0.8,
which implies 0.932KVA
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / msalam_shahin
HP is unit of Power but Kva is unit of load so.... HP & Kva
is different parameter....
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / r.harikrishnan.
1 HP=0.7 KW, KVA=KW/P.F that means 0.7/.85=0.82 KVA.
Is This Answer Correct ? | 4 Yes | 1 No |
What is GNR ? How much value of ground neutral resistance?
MICOM P122 OC/EF RELAY HAVE HARMONIC RESTRAIN OR NOT?
IF TVM OF TRANSFORMER SHOWS POWER FACTOR ON 33 KV SIDE AS 0.97 LAGGING AND ON 132 KV SIDE IS 0.75 LEADING.IS THIS CORRECT.WHERE IS PROBLEM.
What is the polarization index value ? (Pi value)and simple definition of polarization index ?
sail kaott diploma ece ke interviw me qus.kis parkar ke aate hai aur G.S me kya puchate hai kya sameedyaan me kis parkar ke qu.puchate hai
What is the make of breakers, transformers, generators? What are their capacities and ratings?
4 Answers Bharat Bijlee, GHPPL, Tata Motors,
why motors are rated in hp?
how to increase or decrease speed in DC shunt motor by DC convertor
I want to know if it is possible to use Variable Frequency Drive to reduce the current required for starting a motor?
what is practical efficiency of power transformer..?
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED