Why NGR is required for 11Kv geneartor in power plant
Answers were Sorted based on User's Feedback
Answer / rockyxyz
if i am correct NGR is Neutral grounding resistance. NGR
are used to restrict the earth fault current during fault
condition below a certain value. this is done for high
voltage genertors coz due to high voltage & low windng
resistance fault current is very high and the windings are
not designed to carry such a large current so it is the
place where NGR comes to play
Is This Answer Correct ? | 33 Yes | 1 No |
NGR USED IN 11KV GENERATING STATION IS TO LIMIT THE FAULT CURRENT WITHIN THE SPECIFIED LIMIT,Ex: AS PER FORMULA I=V/R,V=11KV.R=63OHM.SO 11000/1.732/63=100A,NGR WILL CONTROL UP TO 100A ONLY BECAUSE GENERATOR IS CONNECTED WITH GRID (SYNCHRONIZED CONDITION)HEAVY FAULT CURRENT MAY OCCURED IN LINE,THAT FAULT CURRENT MAY DAMAGE WINDING INSULATION THATISWHY NGR IS USED TO PROTECT THE GENERATOR FROM HEAVY FAULT CURRENT.I THINK SO
Is This Answer Correct ? | 16 Yes | 2 No |
how can we check a fully charged battery?
what is relation of rpm with Power supply? rpm directly Proposational to power ?
how caculate the pump head to maintain perticuler pressure of water and what would be the motor size in hp for the same?
What is the approximate percentage of Si content in transformer core(CRGO-Cold Rolled Grain Oriented)? Why it is kept so low?
what is the use of starter in tube light?and what it contains
12 Answers L&T, RRB,
what is the difference between id fans and fd fans
12 Answers Perkins Thermal Systems,
how vector surge relay works ?
why we take transformer reading in kva
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
Why we check only first column of root locus..?
1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.
9 Answers CECRI_Central_Electrical_Research_Institute,
WHY RATING OF VCB NOT LESS THAN 630A