we have consol make 3 phase servo stabilizer for cnc m/c.
while installing the earth neutral voltage is 1.7 volts at
stbilizer off condition and when stabilizer get on en
voltage reaches 4.8 volts (new earthing is done and neutral
is helthy condition all phase to neutral volts 440,442,441
v)why this happen.solution for cause.
Answers were Sorted based on User's Feedback
Answer / vishal ingle
Problem looks like in the type & quality of earthing
electodes and pit specifications. if possible try for
another earthing pit with proper watering arrangement.
Note : the earthing pit should be in mother earth & not in
the backfilled soil. (Earthing quality varies with the soil
strata i.e. BC Soil, Hard rock soil, Muroom etc)
Further the earthing pits may be interconnected also to
obtain stabilised results.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a slight loose connection/joint in the neutral wire
if the line voltages are equal.
| Is This Answer Correct ? | 0 Yes | 0 No |
plz check your multimeter. it may be because of corrupted
meter. OR while u measure the voltage keep it away from
Electrical area.
| Is This Answer Correct ? | 0 Yes | 1 No |
I use 20 nos led tube 4feet, in pathway 100mtr approximate, so what size cable i use for lighting
0 Answers Oman Cables Industry SAOG,
How a synchronous generator practically work? what is the function of avr(automatic voltage regulator)in synchronous generator?how the connection of avr to the generator made practically?please give me the answer.
6 Answers Accenture, Heineken,
WHAT IS THE DIFFERENCE BETWEEN UNDERVOLTAGE COIL, CLOSING COIL AND SHUNT TRIP COIL OF AN ACB?
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
What are the types of transformers according to the arrangement of iron cores?
What is the different between conventional MCC and intelligent MCC? Common controller or controller for each bucket
why we use 630mm single core cable for transformer secondary side and why two neutral cable
AC SUPPLY HAVING 230 V FREQUENCY REDUCED ZERO IF MEN TACUCHES THE SUPPLY WEATHER HE GETS SHOCK OR NOT?
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
1)What will happen when 240 VDC supply is connected to 240VAC supply(DC supply +ve is connected to phase of AC supply & DC supply is to neutral of AC supply). 2)Also what will happen when 240 VDC supply is connected to 240 VAC supply in reverse polarity as of Sr. No 1.
What is fault level? How can be calculate the fault level?
through which medium return supply given to alternator please answer in details
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)