what is the difference between series and shunt compensation
using facts in a transmission line
Answers were Sorted based on User's Feedback
Answer / rashid al-hadifi
Series capacitive (series compensation).
To reduce the total reactive power(MVAR)loss.
Shunt capacitive (Shunt compensation).
To improve system power factor.
Is This Answer Correct ? | 49 Yes | 10 No |
Answer / chatinder
shunt compensation is to improve voltage profile.....series compensation is for system stability.
Is This Answer Correct ? | 23 Yes | 8 No |
Answer / kailas vanvas singade
Series compensation reduces risk factor hence it is used to hit the current thermal limit.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / monali bhise
Shunt compensation improves power factor of load whereas series compensation has very little effect on load power factor. For a long transmission line where total reactance is large, series capacitors are more effective for improvement of stability.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mirza
In series compensation voltage is injected into the transmission line while in shunt current is injected....
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / anurag_jammed@yahoo.co.in
by compensation we mean reducing losses,if the load at user
end is inductive in nature we use shunt compensation
(capacitive in nature) while if the load at user end is
capacitive we use series compensation(inductive in nature)
Is This Answer Correct ? | 10 Yes | 25 No |
Answer / saida
compensation is required to put the constant voltage at
receiving end.
the both series and shunt commentators are same but in the
case of series compensator the losses will be more.
Is This Answer Correct ? | 5 Yes | 21 No |
how to check a three phase induction motor by multimeter & megger?
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
what are the current specifications of bus ducts ? i ve seen in IPBD bth 22000 A and 1500 A in 400 kv switchyard . why it is so??
1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.
What should the transformer connection of a 11/220 kV step up and 66/11 kV step down transformer ?
Draw the single line diagram of the power station?
why we use iron corn in transformer instead of wooden core
What is Creepage distance?
how would you determin the horsepower of a motor without a nameplate
Why capacitor bank is not neccessery to switch on,pls answ me with formula
what is meant by loss of field in a DC motor? how a universal motor works?
i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me