control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answers were Sorted based on User's Feedback
Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
Is This Answer Correct ? | 0 Yes | 0 No |
What is cold junction compensation in thermocouples? How is it achieved?
working principle of lvdt?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
can i get model question papers of mahagenco exam?
how we can measure the interface level?is it possible to measure interface level with dp or pressure transmitter?
What is the exact differences between HART,FOUNDATION FIELDBUS,PROFIBUS?
What is the minimum rating availalbe for weld neck orifice in market?
i want to know for good instrument engineer or success how many software knowledage required & from which university
For what Wake Frequency Calculation is used?
What is the Flow rate ?
How many types of sensor
if i change range of flow transmitter in th field then does it need to change range in dcs?