Answer / rakesh jha
A 3-phase transfomer required it's neutral to be grounded.
In delta-delta connection, neutral is not grounded. we use
small star-delta transformer to connect with delta-delta
transfomer and neutral will be grounded.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / zizo
In cases where the neutral point of three phase system is
not accessible like the system connected to the delta
connected side of a electrical power transformer, an
artificial neutral point may be created with help of a
zigzag connected earthing transformer.
Is This Answer Correct ? | 0 Yes | 1 No |
what are the available sizes of pin type terminal lugs in the market today?
A three phase transformer 460v primary 220v secondary (three phase four wire system.) Why did we get 460 volts across the neutral on the secondary side?
4-Why we measure the insulation resistance of main core and frame in spite of that must be connected with ground before energize the transformer?
what is bausbar?
What is the Ramping rate of Generator. What mena Ramping rate
what happen if the secondry winding of the transformer is having less no of turns compare to the primery winding.
what is the effect of un-synchronized power.
Can the same motor be operated in both direction ?
What is meant by control system?
how to calculate the voltage drop in electrical cable while laying cables?
The knee point of a current transformer is normally unique and known.So why in the nameplate of a CT they put the minimum value like this Vk> 400v.
is it possible for different brand of H.V transformers to run or operate in parallel to each other? if so how much disturbance can this affact the H.V bus bar?