in transformers for ex. 100mva and 400kv the secondary
current is about 420 amps but for selection of bushing the
capacity of selected bushing is 2000A why there is such
big difference ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The insulated leads of secondary from the Tr windings are
taken through hollow rods inside the bushing and connected
at the top.As the rod has to bear the all the mechanical
forces like torsion and strain, the wall has to be thick enough.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
I must have used the word 'pipe' instead of rod.Further,in
the condenser type bushing the oil inside is locked and
isolated from the oil in the tank.Hence it is deprived of
cooling. The pipe should be of much higher capacity to avoid
heating up due to the current flowing through it.
Is This Answer Correct ? | 0 Yes | 2 No |
how is the incoming cable size calculated for a given current rating of a panel??
What does Bode plot tell you?
A separately excited dc motor having 2 ohm armature resistsance draws a current of 10A and torque developed is 20 Nm under rated field condtion. the speed of the motor under the rated field condtion , when it is connected to a 100V DC source and delivering 10Nm torque....
what is the working principle of Brushed alternator ? without exictation how we can give dc supply to rotor ?
how do we know the LT or HT panel trip by some broblem which indication willshow
how to calculate the KVAr for an motor for improving the PF
What are the test performed on A faulty transformer ?
What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
The following equipment are installed ia a plant 1. 110KW Induction motor 4 Nos 2. 30 HP motor 3 Nos 3 15 HP Motor 3 Nos 4 7.5 HP motor 4 Nos what is total load of plant if one of each is stand by.
the transient state stability limit of a system wherin power is transmitted throgh a double transmission line is (a)equal to steady state stability limit (b)more than its steady state stability limit (c)less than than its steady state stability limit (d)equal to its dynamic stability limit
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?