Answer / baljinder singh
tap changer is the part of transformer's secondary winding
which is use to increase and decrease the output voltage of
the transformer.
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / bharani
Transformers in general can have tappings in both primary
and secondary.
When we talk of HT transformers, tappings are provided in
the primary winding, this helps us in getting proper output
voltage by changing the tapping whenever the HT voltage
varies from the actual specified voltage.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / byd
i am working at Transformer factory as test engineer, tap
changer is the part of transformer's primary winding which
is use to balance secondary voltage, for example we
have transformer which feature are: 630kva, 33/0,400 kv,
and this transformer has a tap changer , transformer
primary voltage positions are like these
HV(v) Lv (v)
28500
30000
31500
33000 ....... 400 v
34500
36000
network voltage is 33000v but sometimes it can be
increase or decrease , you can change tap changer:)
but this for no-load tap changer for distrubition
ransformer, if it is power transformer you should use
load tap changer
Is This Answer Correct ? | 9 Yes | 3 No |
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
which motor will u use in refinaries?
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.
Multi-step core is used in transformer to: A) Increase the output B) Decrease the cost of core material C) Decrease the cost of copper D) Increase the efficiency
Percentage losses in power generation?
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
why we not using 230kv directly why we are stepping down and then stepping up
what happen if i change the polarity of ac when it is connected with motor
11kv/433v delta/star distribution transformer primary side full load Ht current is 83.33A in , but input side VCB rating 800A.why?
How to calculate percentage impedance of a power transformer.
what is the relation between frequency and inductive reactance in a d.c supply?
Why is the neutral point of a star connected winding of a motor not grounded?