what is the procedure for erection of a transformer
Answer / debasis sahoo
During installation of Transformer on a Pole mounting structure, following checks should be made:
Ensure that the base channel of transformer is at height complying to IEC Standards:
a) Height of top of HV bushing from ground for pole mounted transformer should be 4.572 meters minimum (15 Ft)
b) Height of top of HV bushing from ground for plinth mounted transformer should be 2.75 meters minimum (8 Ft)
Ensure that base channel is horizontally leveled
Avoid jerky movement of the transformer while lifting it upwards during installation
During installation ensure that the HV bushings of the transformer are on the DO unit (or HG fuse unit) side of the structure
After installation of transformer, also check that other allied equipments such as AB switch, Horn Gap fuse units, DO Fuse sets, Lightening arrestor etc. are fitted at appropriate positions as per the applicable drawing issued by the utility.
Use PVC unarmoured cable (3 ½ core) of appropriate size and length for LV side. Ensure that the lugs are appropriately crimped at the ends.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the safety of VCB.
5 Answers Nagarro, Roto Power, RotoPower,
If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer
how the synchronizing is obtained at bus couplers in grid substation? (because there we cannot change the frequency in one of transmission lines like in generator synchronization)
A heater capacity is 3.0 KW on 415V . if supply voltage is 380Volt . what is heater capacity on 380volt . and how calculate and give formulas . Prakash veer singh Roto power Engg.
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
What are the material used for resistor?
how u measure/calculate renge of capacitor,capacitor has no any rating tag.what is the theory of measure of capacitons.
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
When we give supply to a transformer 11 kv and we get 415v from it, so when we give supply to same transformer 415v on ht side what we get? and When we gives supply to any transformer to L.T. side 415v or 220v What supply is on H.T. side?
what is the different betweem earthing and neutral?
why root three is used and how its comes in three phase power system?
In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)