how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?
Answers were Sorted based on User's Feedback
Answer / komal
1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ashwin jain
if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / haridass
1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.
2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mr.georgemathews
It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.
The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.
This whole process will hardly take 5 min.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range
| Is This Answer Correct ? | 0 Yes | 0 No |
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?
what is Instrumentation?
What materials are used in thermo wells?
What is the use of temperature compensation?
What is duty of as-built engineer.
why we use -ve voltages in vibration prob?
what u mean by speed control in turbin? how it was working?
What is the exact differences between HART,FOUNDATION FIELDBUS,PROFIBUS?
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
if differential pressure created by orifice falls below vapour pressure of liquid flowing through it what will happen
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)