whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.
Is This Answer Correct ? | 13 Yes | 5 No |
Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.
However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.
Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)
Is This Answer Correct ? | 5 Yes | 6 No |
how to convert the KVAR to microfarad??????????????????
which type your UPS on line,off line give the reason?
In underground cables,we have a grading method called 'capacitance grading'.Why is it called 'capacitance grading' although we do not use any capacitor in it?
in industrial lighting in each circuit how many lamps can be given? and how much load can be put on each circuit? is there standard for this? please help me with the standard description?
WHAT HAPPEN IF TRANSFORMER HAS GIVEN SQUARE WAVE SUPPLY
I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far from transormer), it still poor. Can anybody explain it??
Why Delta Star Transformers are used for Lighting Loads.
what is the formula for hv test for cable and circuit breaker..????
How does a clampmeter measures dc current
DG drop how much freqency at 100% load?
how to select rating of HT Panel
What are the conditions to be satisfied before connecting two DC generators in parallel?