what the differant between Wet Leg /Dry Leg
Answers were Sorted based on User's Feedback
Answer / www.islamqa.com
They are diffrential pressure transmitter "installation
technique" used in "level measurement"
When installing diffrential pressure transmitter we attach 2
impulse lines with high & low transmitter sides, the 1
attached to low side is empty impulse line so it is "dry
leg" or it's filled with a sealing liquid with density
greater than the process liquid so it is "wet leg".
We use "dry leg" for closed pressurized tank.
We use "wet leg" for closed pressurized tank also but if we
have the probability of process liquid condensable vapor
which will give a faulty measurement.
If we have an open tank, the Tx low side is atmospheric.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
ahmedsabry.onine@gmail.com
Is This Answer Correct ? | 33 Yes | 0 No |
Answer / heri santoso
Dry and Wet leg are process connection of dp cell level
instrument used in close tank
(Wet leg)Where leg impulse connection of tx contained fill
(difference SG)with process fluid in tank.fill is a
parameter reading of tx tranduser
(Dry leg)where leg impulse connected to atm no fluid in leg
connection
Thanks
Is This Answer Correct ? | 3 Yes | 11 No |
if in a level tx height is given, how u calculate the ranges of the tx?
2 Answers Bombay Rayon Fashions, Invensys,
What is limitation of the ht.of the displacer of a level trol?
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
hello dear i have faced problem in drum level transmitter. the problem is when i engrize the meter meter shows 100% but the actual level 40 or something plz suggest me
What is the use of the shield wire and how is the connection at both the ends of a shield wire?
what are the definitions of input, output, command & signal according to instruments controlled by PLC using DCS System?
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
Which of the following instruments consumes maximum power during measurement?
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
Can we use mov instead of esdv Explain the reason
what is the diffrene between DCS System and PLC System
How DP Transmitter can be calibrated for crud application in floating roof tank?