how to check IR values in alternator winding?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Isolate all phase windings at both ends and measure IR of
each phase to body and between windings
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / subash
A. Purpose and Theory
The IR test measures the resistance of the electrical
insulation between the copper conductors and the core of
the stator or the rotor. Ideally this resistance is
infinite, since after all, the purpose of the insulation is
to block current flow between the copper and the core. In
practice, the IR is not infinitely high. Usually, the lower
the insulation resistance, the more likely it is that there
is a problem with the insulation.
PI is a variation of the IR test. PI is the ratio of the IR
measured after voltage has been applied for 10 minutes
(R10) to the IR measured after one minute (R1), i.e.:
PI = R10/R1
A low PI indicates that a winding may be contaminated with
oil, dirt, insects, etc. or soaked with water. In the test,
a relatively high DC voltage is applied between the winding
copper and the stator or rotor core (usually via the
machine frame). The current flowing in the circuit is then
measured
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / nithin
Insulation resistance of alternator is checked using a megger and before measuring it the connections to the protective devices like CT,PT and also the connection to the AVR to be disconnected. Then the star connection of the winding to be disconnected ,then we can check IR value
Is This Answer Correct ? | 0 Yes | 0 No |
why ht line fuse wire is so thin
how can i select the cable ratings
What is complex power?
how we select fuse rating for motor?
can we replace d.c.motor by 3 phase induction motor for a particular application
What is the life of MCCB
What is meaning of star delta connection / delta star connection and which one is best and what is the advantage?
IN THE CASE OF AN ELCB, IF THERE IS ANY UNSTABILITY BETWEEN PHASE AND NEUTRAL IT MAY TRIP. BUT MY QUESTION IS WHEN A LOAD IS CONNECTED IN BETWEEN P AND N, THE LOAD CONSUMES SOME POWER AND THERE IS A DIFFERENCE IN NEUTRAL WITH RESPECT TO THE PHASE. THUS ACCORDING TO ME, THE ELCB WILL AUTOMATICALLY OPERATES WHEN EVER THE LOAD CONSUMES-- I KNOW IT IS WRONG. BUT THE SOLUTION IS?????????
Why Humming noise originated in Starter motor and how it was generated ?
whay we transmit power in 3phase no in 4 or 2 or 5......etc?
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
What happens on the secondary of a 33kV/11kV when one phase of the primary fuse blows?