how pressure reduce through pressure control valve? suppose
we have to reduce 20 kg pressure to 10 kg pressure , then
what we do ? open the valve or close the valve , initially
it is 20 % is upon ( for ur knowledge ).
Answers were Sorted based on User's Feedback
My dear,
In control valve we ll compare the setpoint(operator interference value) and the actual pressure on the line.this deviation is given to the control valve.When the error is positive(means pressure is high),the C/V starts closing and when the error is negative(means pressure is low),the C/V opens and maintains the pressure.
One more thing,why u need to fix the low limit of control valve to open 20%.Depending on the deviation the controller controls the process pressure.
Finally,the controller tuning is must for this control.play with the gain and integral time and deadband to make steady process..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / daxish_02
If pipe size is same before and after so this answer is correct..
basic fundamental behind the general formula that is
pressure=force/area......ok
here pipe size is fixed...ok
assume 20% valve open....than area of pipe cover after the valve is more so we get some pressure..
assume that valve open 40% so area of material flowing through valve increase so pressure decrease after the valve.....
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / g.s.arun
to open the byepass valve ,to reduce the pressure 20kg to 10 kg.
| Is This Answer Correct ? | 1 Yes | 4 No |
Speedtronic system .
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
How does electro magnetic pump works ?
what is the difference b/w magnetic flow meter&mass flow meter? which one is best?
What is the Difference between CNC and PLC
What is the principle of a Pressure gauge?
What is cavitation. what is the effect of it on control valve and how is it prevented.
What is the difference between compensation and extension cable.
please tel me the calibration of pneumatic controler.
How to change dcs card in online. (Dsc is maxdna)
A DP transmitter is used to measure the level of an open tank. The drain line of the tank is connected to a control valve, and is configured as, if the level of the tank is 90% the valve should get open 10%. And if the tank level is 10%, the valve should get open 90%. Draw wiring diagram and explain how to configure DP transmitter and control valve using HART communicator. If the span error at output is 1%, what will be the %opening of the control valve at 60% level of the tank?
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)