Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What happen if 1200KW/1500KVA alternator runs at no load
and high R.P.M.for one minute?

Answers were Sorted based on User's Feedback



What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / dr.d.m.kothari

This will never happen because AVR and giverning
arrangement.Governor always control speed according to load.

Is This Answer Correct ?    9 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / subodhkhivsara

If prime mover runs very high speed (without any control)
within a fraction of second rotor damaged and after that
Excitation system damaged.It will goes very dangerous
mode.So Never run Alternator without control.

Is This Answer Correct ?    5 Yes 1 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / gurucharan singh

Generator loading & No load running has no effect its
paramaters, means generator run at no load as required.
Second part of question, generator are normally designed to
1.2 to 1.5 times of nominal speed to run for one minute
without any problem. Very generation system has a speed
controller & voltage controller which responce to these
condition within 1 to 2 seconds. I suggest interviwer shall
not confuse to candidate at interview.

Is This Answer Correct ?    2 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / k.prakashchandra

There are over speed and over voltage relays to
protect.Governor becomes helpless if there is sudden throw
off of load,then over speed relay of the governor shuts down
the prime mover.With AVR, voltage does not increase.However
generators are designed to withstand runaway speeds for
short periods. Bearings are first to get damaged under
prolonged high speeds.Governors can also be made not to
allow for undesired high speeds with the help of braking
systems, if they are employed.

Is This Answer Correct ?    1 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / k.prakashchandra

The above is applicable to hydro-generator

Is This Answer Correct ?    1 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / n r@jesh

D.G runs No load condition out put voltage will generated
high so, system protection will damaged

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)

0 Answers   UOG,


how many test is necessary for 27mva transformer.

3 Answers   HEG,


Difference between low impedance and high impedance Restricted Earth Fault

0 Answers  


In radial network the source is fed from 1 end both ends at central

0 Answers  


Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?

1 Answers   Bhel,


What is CBCT ? Why & Where it is used?

14 Answers   BCT,


what is pure resistive circuit and pure inductive circuit

1 Answers  


load increase means 1 resistance increase 2 load resistance decrease 3 current increases through load 4 none of these

3 Answers  


After fault clearing in Tr line, whether the Metering core of CT is comes to normal condition from saturation region & its works as a normal condition?

1 Answers  


what is meant by negative conductor?

2 Answers  


what will happen if u run induction motor beyond its rated speed

13 Answers   Adani, BARC, Bescom,


full form of electrical?

0 Answers   CEAT,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)