when running 2 nos 450kva dg sets in parallel operation ,in
one Dg set power factor and Kvar going to lagging and ampere
suddenly going high,please give me suggestion to correct the
same.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
May be due to over excitation.If you are using AVR ,run on
manual channel to check the PLC and auto channel
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / nithi
mr.prakash answer is correct........over excitation of one
DG set & under excitation of another Dg set will lead to
this type of problem.so, check both DG set AVR circuitary
(voltage set value).
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the effect on 3phase induction motor if current setting knob of DOL kept at minimum current?
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
What is the impedence of Transformer?
what is the difference between DOL starter&star-delta starter& automatic star-delta starter
why we not connect the 12 V batteries in parallel to get the more backup supply for an UPS ? wheter off line or on line UPS ?
What does dny11 stand for?
wat do knw aboot circuit breakers ?
Why 5kv megger used to megger 6.6kv motor or 33kv transformer why not 500v?
Why scr and igbt used in ups systeam ????
what happen when increase or decrease size of lamp,light.glass.
how Local Breaker Backup relay working?
Please mention available current rating for MCB,RCCB,MCCB in the market or any website
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)